I have an existing RSLogix 500 ladder of 85 rungs. Its sole purpose is to control electric motors, specifically handling precise speed regulation and motor/cabinet use. This RSS needs to be rewritten into Click Plus C2-01-CPU-2. A-B plc has failed and being replaced to Click. Here is what I need: • RSLogix 500 translated into the Click Plus software environment. • All rungs organised logically, with clear rung comments and tag names so future maintenance is simple. • A brief overview (PDF or Word) describing the control strategy, the registers/timers you used, and how to tweak set-points.
Project ID: 40780433
118 proposals
Remote project
Active 19 hours ago
Set your budget and timeframe
Get paid for your work
Outline your proposal
It's free to sign up and bid on jobs
118 freelancers are bidding on average $441 USD for this job

Precision motor control and industrial automation are central to my engineering background, making me well suited to translate your 85-rung RSLogix 500 program for the Click Plus C2-01-CPU-2 replacement. My experience with PLC, SCADA, HMI and DCS integration, combined with control engineering and electrical engineering expertise, supports a careful migration of the existing motor speed and cabinet-use logic. My work in precision motor control, including FOC and PID, gives me a strong understanding of speed regulation, set-points, timers, registers and control behavior. I can also structure the Click Plus ladder with clear tag names and rung comments, then provide the requested PDF or Word overview documenting the control strategy and adjustment points for easier future maintenance. I would be glad to apply my automation and control experience to this PLC conversion and deliver a clear, maintainable Click Plus program.
$750 USD in 7 days
8.5
8.5

Hi, I am an embedded systems engineer with over 16 years of experience. I have extensive experience with PLC programming and motor speed regulation, including refining existing ladder logic for reliable operation and straightforward maintenance. I can expand and refine your RSLogix 500 project within the 85-rung target, keeping the focus on closed-loop speed control and the required safety permissives. I’ll review the existing logic and feedback arrangement, then refine the control loop and organise the rungs with meaningful symbols and clear comments. I’ll deliver the updated .RSS file, verified to compile without errors for the selected PLC, plus a brief PDF explaining the control strategy, registers, timers, and set-point adjustments. I can also support initial tuning using feedback from your equipment. Which PLC model are you using, and how are speed feedback and motor drive commands connected? Reviewing your existing .RSS file would help me confirm the scope. Please contact me to discuss details.
$725 USD in 7 days
7.7
7.7

Hi, I understand you need the existing RSLogix 500 project expanded into about 85 clear, documented rungs for reliable closed-loop motor speed control. I will review the current ladder file, organize the logic, set clear tags and rung comments, and keep safety permissives limited to what is needed. The program will be checked for compile errors and the control registers, timers, scaling, and set-point adjustment process will be explained in a short PDF or Word guide. My C Programming, Electrical Engineering, and Automation experience helps me build control logic that is practical to maintain, while keeping the final work focused on your existing PLC hardware. Which RSLogix 500 processor, analog input/output addresses, feedback device, and required speed-control range should the program use? Please start the chat and let’s discuss the current file, motor feedback, and speed-control details.
$650 USD in 10 days
7.3
7.3

Hi there, I am excited to assist you with your RSLogix 500 Motor Speed Program. With extensive experience in PLC programming and motor control systems, I understand the importance of having a precise and reliable closed-loop speed control system. My background in C Programming, Electrical Engineering, and Embedded Systems aligns well with your project needs. I will ensure your ladder logic is meticulously organized, with each of the 85 rungs clearly commented and logically structured for straightforward maintenance. By focusing on seamless integration and precise control, I will utilize appropriate registers and timers to achieve robust speed regulation while adhering to safety standards. To help you better understand the implemented solution, I will provide a comprehensive overview document that details the control strategy, the use of specific timers and registers, and guidance on adjusting set-points. This will empower you or your team to easily tweak parameters in the future. Let’s work together to refine your existing project into a system that ensures dependable motor speed control. I am eager to apply my skills to help you achieve your goals. Best Regards,
$250 USD in 10 days
6.8
6.8

Hello, I can help refine your existing RSLogix 500 project into a well-organized ladder program targeting approximately 85 documented rungs, focused on closed-loop motor speed regulation. My background is in electrical engineering, control systems, and embedded electronics. I will review your existing logic and PLC hardware configuration before defining the speed-control strategy. I can organize the rungs into logical sections, add clear rung comments and meaningful register descriptions, and implement suitable set-point handling, feedback scaling, safety permissives, and fault monitoring based on your actual hardware. I will also prepare a concise PDF or Word document explaining the control strategy, registers, timers, tuning parameters, and maintenance procedures. Please share your existing .RSS file, PLC model, motor drive/VFD model, speed feedback type, and current I/O mapping so I can assess the required changes and compatibility. Inshallah, I will aim for clean, maintainable logic and verify compilation against the available RSLogix 500 environment. Regards, Engr Muhammad Usman
$500 USD in 3 days
6.9
6.9

Your RSLogix 500 migration requires careful handling of motor control, speed regulation, and replacement hardware, and my 8+ years in embedded products and electrical/electronics development give me a strong foundation for translating control logic accurately into a new environment. My background includes industrial communication and control technologies such as RS485, Modbus RTU, PWM, ADC, UART, SPI, and I2C, along with C programming and embedded systems development. This is relevant to preserving the existing motor and cabinet-control behavior while adapting the logic to the Click Plus C2-01-CPU-2. I can also structure the converted program with meaningful tags and comments, then provide clear documentation covering the control strategy, registers, timers, and set-point adjustments. I am committed to producing a maintainable, well-documented conversion and would be glad to take responsibility for this RSLogix 500 to Click Plus migration.
$500 USD in 7 days
6.9
6.9

My control-engineering and PLC experience, combined with a systems-level background in electrical engineering, electronics, embedded systems, and software, directly fits this motor speed-control project. I develop control logic for embedded devices and PLC-based automation, with a strong focus on reliable integration between hardware and software. That foundation is valuable for refining your existing RSLogix 500 ladder file into a clear, maintainable program focused on closed-loop motor speed regulation and safety permissives. I can structure the logic toward the approximately 85-rung target, use meaningful tags and rung comments, and prepare the accompanying documentation covering the control strategy, registers, timers, and set-point adjustment. My multidisciplinary engineering experience also helps ensure the ladder logic reflects the real electrical and control behavior of the motors rather than functioning as isolated code. I would be glad to take ownership of this RSLogix 500 refinement and deliver a clean, documented solution aligned with your existing PLC platform.
$750 USD in 7 days
6.7
6.7

My electrical engineering, electronics, embedded systems and automation background is directly aligned with refining an RSLogix 500 motor-control application. I can work within the existing PLC platform and focus the program on closed-loop speed regulation, safety permissives, and a clean structure near your 85-rung target rather than adding unnecessary start/stop or direction logic. My engineering approach is supported by extensive technical automation and process work, including construction scheduling, complex control-style spreadsheets, and process automation projects completed for clients across the US, UK, Australia, Europe and the Gulf. I will provide clearly named tags, logical rung organization, useful comments, and supporting documentation covering the control strategy, registers, timers, and set-point adjustments. I also understand the importance of a maintainable file that compiles cleanly and can be supported by the next engineer. I am ready to apply my automation and electrical engineering skills to produce a dependable, well-documented RSLogix 500 motor speed program and its accompanying overview.
$500 USD in 7 days
6.1
6.1

Hi, I've read your requirement. The main job here is getting the closed-loop speed control right. I'd need to get four things right: Feedback: scale the encoder or tachometer signal accurately so the PLC sees the true speed. PID loop: run it at a fixed update rate (timed interrupt), not once per scan, so the response is consistent. Setpoint ramping and output limits: the motor speeds up and slows down smoothly without overshooting, hunting or saturating the drive. Safety permissives and faults: stall, overspeed and feedback loss, so the loop drops to a safe state instead of running away. All of this has to fit cleanly into about 85 rungs on top of your existing logic. What you'll get: An expanded .RSS program with a logical rung structure (scaling, ramp, PID, output, permissives, alarms), full rung comments and clear symbol names No errors in RSLogix 500 Verify Project A short Word or PDF document covering the control strategy, the register, timer and PID block map, how to change setpoints, and a step-by-step tuning guide To start, please send: The current .RSS file The processor model (SLC 5/0x or MicroLogix) The number of motors, and the drive make and model The speed feedback type, and the analog I/O cards with their slot numbers The PID gains I deliver will be solid starting values. I look forward to working with you. Best regards, Steven
$500 USD in 3 days
5.8
5.8

Hello sir I'm PLC programmer with 10 years of experience in the automation field I have good experience with rs logic 500 software and I do alot of jobs using it I have all version of rs logic 500 with my own license I have also good experience with click and automation direct product I also have good experience with studio 5000 and I do alot of jobs using it Please contact me for more detailes I hope we can work together Best regards
$500 USD in 7 days
5.6
5.6

My electrical engineering and embedded-systems background is well suited to refining a motor-control PLC program where reliable speed regulation and safety permissives matter. I work with C programming, electronics, and control-oriented embedded systems, giving me a strong foundation for understanding feedback signals, register handling, timing, and motor behaviour. I can apply that technical perspective to your existing RSLogix 500 ladder file, keeping the program focused on closed-loop speed control rather than unnecessary start/stop or direction logic. Clear tag naming, rung comments, logical organisation, and the accompanying control-strategy documentation are important for making the final program maintainable and practical to tune. I would be glad to refine the project toward the approximately 85-rung target and deliver a clean, documented control solution. Choose me to bring the electrical and embedded-systems understanding this motor application requires.
$500 USD in 7 days
5.2
5.2

Run the RSLogix 500 speed loop at a fixed update interval, with feedback scaling checked before tuning. Check whether the drive already closes the speed loop—two competing loops can cause hunting rather than improve regulation. I’ll refine the existing file with output limits, feedback-loss handling and safety permissives, without adding unrelated start/stop or direction logic. In 3 days, you’ll get an error-checked .RSS targeting 85 rungs maximum, clear comments and symbols, plus a brief PDF covering control strategy, registers, timers and set-point adjustments. Final tuning will use live motor feedback. Can you share the existing .RSS file? Sid Techno LLC
$275 USD in 3 days
4.8
4.8

Hi, I am Adeel. I would start by reviewing the existing rungs and mapping every input and output, so the speed loop sits on a clean base. The first decision is how speed is measured and set, whether by encoder or tachometer into a high speed counter or analog input, and whether the drive takes a 0-10V or 4-20mA reference. I would then build the closed-loop control with clear set-point, scaling and limit tags, keeping the safety permissives in their own separate rungs. What feedback device is fitted to each motor? Over 10 years I have completed 161 projects here and I am in the top 3% of freelancers, as a Microsoft Certified Solution Developer. I am just a message away whenever you want to talk through the feedback and drive interface.
$250 USD in 3 days
4.9
4.9

Hello, We are a team of two consisting of an Electrical Engineer and an Electrical Controls Specialist with over 50 years of combined industrial experience in automation, PLC programming, troubleshooting, and control system upgrades. We have extensive experience with Allen-Bradley systems, including RSLogix 500, Studio 5000, and converting older equipment to newer PLC platforms. Before proceeding, we would like to review your existing program and motor control configuration to ensure the CLICK PLUS can provide the same functionality, particularly motor speed regulation, I/O, and communications. One question we have is what model Allen-Bradley PLC failed and whether the equipment is currently down. We have spare A-B controllers available that may provide a quicker solution to getting your equipment operational while the CLICK PLUS conversion is being developed, potentially reducing downtime and costs. We can provide a well-organized, documented PLC program with rung comments, descriptive addressing, and an overview of the control strategy, registers, timers, and setpoints. We are located in Oregon (Pacific Time), and our rate is $125/hour. Availability and project timelines can be discussed after reviewing the program. Feel free to reach out with any questions or to schedule a meeting. Bid and deliverables are placeholders until details are discussed.
$2,500 USD in 30 days
4.9
4.9

Dear Client, I can review your existing RSLogix 500 project and complete the ladder logic around stable, closed-loop motor speed control. I would first review the PLC model, motor drive/VFD interface, speed-feedback signal, current rung structure, and how the speed set-point is generated. From there I can organise the logic around permissives, scaling, feedback, set-point handling, and fault conditions while keeping the project close to your 85-rung target. I can provide a complete, well-documented RSLogix 500 (.RSS) project with clearly structured ladder logic, meaningful rung comments and register descriptions, closed-loop speed control, set-point and feedback scaling, and a concise PDF/Word guide explaining the control strategy and adjustment parameters. The final program will be checked for compile errors and kept within the required rung count. I prefer reviewing the existing file before suggesting unnecessary changes, especially since you want to retain the current RSLogix 500 platform. One question: which Allen-Bradley PLC and motor drive/VFD are being used, and what signal provides the actual motor-speed feedback? Send me the existing .RSS file and those details, and I can determine the cleanest way to complete the program. Kind Regards Prat PCB Must Innovations
$465 USD in 7 days
6.1
6.1

Your 85-rung motor-control program requires careful electrical and engineering understanding, especially where precise speed regulation and cabinet operation are involved. My background in Electrical Engineering, Electronics, and C Programming gives me a solid foundation for working with PLC-based motor control and translating control logic accurately into the Click Plus C2-01-CPU-2 environment. I can produce a logically organised Click Plus program with clear rung comments and meaningful tag names to support future maintenance. I will also provide a concise PDF or Word overview documenting the control strategy, registers and timers used, and the set-points that can be adjusted for operation and tuning. My engineering-focused approach will help preserve the intent of the failed Allen-Bradley system while making the replacement program understandable and practical to maintain. I would be glad to take responsibility for this RSLogix 500 to Click Plus conversion.
$250 USD in 5 days
4.5
4.5

I understand you need a robust RSLogix 500 motor speed control program, similar to projects where I've implemented PID loops for precise process variable regulation within tight tolerances. My expertise lies in translating complex control requirements into efficient and maintainable ladder logic. My approach will involve developing a structured ladder file leveraging RSLogix 500's built-in PID instruction for closed-loop speed control. I'll utilize a combination of analog input scaling for feedback, a pre-tuned PID algorithm for accurate motor speed regulation, and safety interlocks integrated as permissives to ensure safe operation. Rungs will be logically grouped (e.g., initialization, feedback processing, PID calculation, output scaling, safety checks) with comprehensive rung comments and descriptive tag names following a consistent naming convention for clarity. Could you provide details on the specific motor type and its feedback mechanism (e.g., encoder resolution, analog tachometer)? Also, what are the target speed accuracy requirements and any specific environmental considerations? I'm available for a brief call to discuss these further and outline the implementation timeline.
$599 USD in 21 days
4.3
4.3

Hello, I am an experienced Automation Engineer with expertise in Allen-Bradley PLCs and RSLogix 500. I can convert your 85-rung ladder logic to CLICK PLUS C2-01-CPU-2, maintaining the original motor control functionality, with clear rung comments, organized tags, and a concise document explaining the control strategy and set-point adjustments. Please share the existing RSLogix 500 project file and I/O details to get started. Best regards
$500 USD in 7 days
4.5
4.5

Hi, Adelman here from Texas RSLOGIX 500 CLOSED-LOOP MOTOR SPEED CONTROL - you need reliable speed regulation in a clean, documented ladder program within 85 rungs. I’d organize the logic into clear control sections, with documented registers, speed feedback, set-point handling, and safety permissives. I’d also check fault conditions and verify the logic against your actual PLC setup. Which SLC 500 processor and motor speed feedback method are you using? Looking forward to work with you.
$500 USD in 5 days
4.0
4.0

Hello, I am interested in developing your RSLogix 500 Motor Speed Program. I have a strong understanding of PLC programming, industrial automation, and motor control systems, and I can help create a reliable program that meets your specific operational requirements. I will review your project specifications and determine the appropriate control logic for accurate and efficient motor speed management. I will develop and configure the RSLogix 500 ladder logic to support the required motor speed control functions, including start/stop operations, speed adjustment, interlocks, and safety conditions as needed. I will also review the PLC inputs and outputs, troubleshoot potential logic issues, and ensure the program is structured clearly for easy maintenance and future modifications. If required, I can assist with integrating the program with the relevant motor drive or variable frequency drive (VFD). My priority is to deliver a well-organized, reliable, and thoroughly tested PLC program that performs according to your requirements. I can provide the completed RSLogix 500 project file, documentation of the control logic, and support with testing and troubleshooting. I look forward to discussing your motor specifications, PLC hardware, and desired speed-control method so we can achieve the best possible results for your project.
$250 USD in 7 days
3.9
3.9

Mount Airy, United States
Member since Oct 22, 2026
₹1500-12500 INR
$100-200 USD
$8-15 USD / hour
₹100-400 INR / hour
$30-250 USD
₹100-400 INR / hour
$100-200 USD
€12-18 EUR / hour
$25-50 USD / hour
£250-750 GBP
₹1500-12500 INR
$250-750 USD
$10-300000 USD
₹1500-12500 INR
£10-20 GBP
₹600-1500 INR
₹750-1250 INR / hour
$30-250 USD
$30-250 USD
$30-250 USD